compressor cycles fast - no cooling
I was going to add refrigerant, assuming that was why the compressor was short cycling but stopped as soon as I saw these pressures. I began looking for a bad low pressure sensor after reading some of the comments above.
You can can loopback the pressure switch simply by taking a little piece of wire (strip the ends back about 1/4"), pull off the connector, and short the 2 points together with it. It should force the compressor to run, but I wouldn't leave there if the pressure doesn't want to maintain, but it seems like a way to get your added coolant circulating. So far I'm having pretty good luck!
I've added refrigerant to 45 psi and the cycling has stopped. The duct air temp has dropped from 90 F to 69 F (ambient was 91 F here in sunny Michigan).
Thank you for your help.
Chris Z
You can can loopback the pressure switch simply by taking a little piece of wire (strip the ends back about 1/4"), pull off the connector, and short the 2 points together with it. It should force the compressor to run, but I wouldn't leave there if the pressure doesn't want to maintain, but it seems like a way to get your added coolant circulating. So far I'm having pretty good luck!
CZ